Re: Kaskadierter Huawei Wechselrichter - Modulkonfiguration PV
Verfasst: Sa Feb 03, 2024 3:14 pm
Meldung aus Status:
Hier mal das Log
Code: Alles auswählen
Modulmeldung:
modules.common.modbus <class 'modules.common.fault_state.FaultState'> ('modules.common.modbus Exception Response(131, 3, IllegalValue)', <FaultStateLevel.ERROR: 2>)
Code: Alles auswählen
2024-02-03 16:08:10,239 - {root:74} - {INFO:MainThread} - # ***Start***
2024-02-03 16:08:10,294 - {modules.common.component_context:51} - {DEBUG:device0} - Update Komponenten ['Huawei Zähler', 'Huawei Wechselrichter']
2024-02-03 16:08:10,301 - {modules.common.component_context:24} - {DEBUG:set values cp2} - Update Komponente ['Ladepunkt']
2024-02-03 16:08:11,049 - {modules.common.fault_state:55} - {ERROR:device0} - Huawei Zähler: FaultState FaultStateLevel.ERROR, FaultStr modules.common.modbus <class 'modules.common.fault_state.FaultState'> ('modules.common.modbus Exception Response(131, 3, IllegalValue)', <FaultStateLevel.ERROR: 2>), Traceback:
Traceback (most recent call last):
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 90, in __read_registers
raise FaultState.error(__name__+" "+str(response))
modules.common.fault_state.FaultState: ('modules.common.modbus Exception Response(131, 3, IllegalValue)', <FaultStateLevel.ERROR: 2>)
The above exception was the direct cause of the following exception:
Traceback (most recent call last):
File "/var/www/html/openWB/packages/modules/common/configurable_device.py", line 36, in __call__
self.__updater(components_list)
File "/var/www/html/openWB/packages/modules/devices/huawei/device.py", line 31, in update_components
regs = c.read_holding_registers(32064, [ModbusDataType.INT_32]*5701, unit=modbus_id)
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 123, in read_holding_registers
return self.__read_registers(
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 105, in __read_registers
raise FaultState.error(__name__+" "+str(type(e))+" " +
modules.common.fault_state.FaultState: ("modules.common.modbus <class 'modules.common.fault_state.FaultState'> ('modules.common.modbus Exception Response(131, 3, IllegalValue)', <FaultStateLevel.ERROR: 2>)", <FaultStateLevel.ERROR: 2>)
2024-02-03 16:08:11,052 - {modules.common.fault_state:55} - {ERROR:device0} - Huawei Wechselrichter: FaultState FaultStateLevel.ERROR, FaultStr modules.common.modbus <class 'modules.common.fault_state.FaultState'> ('modules.common.modbus Exception Response(131, 3, IllegalValue)', <FaultStateLevel.ERROR: 2>), Traceback:
Traceback (most recent call last):
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 90, in __read_registers
raise FaultState.error(__name__+" "+str(response))
modules.common.fault_state.FaultState: ('modules.common.modbus Exception Response(131, 3, IllegalValue)', <FaultStateLevel.ERROR: 2>)
The above exception was the direct cause of the following exception:
Traceback (most recent call last):
File "/var/www/html/openWB/packages/modules/common/configurable_device.py", line 36, in __call__
self.__updater(components_list)
File "/var/www/html/openWB/packages/modules/devices/huawei/device.py", line 31, in update_components
regs = c.read_holding_registers(32064, [ModbusDataType.INT_32]*5701, unit=modbus_id)
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 123, in read_holding_registers
return self.__read_registers(
File "/var/www/html/openWB/packages/modules/common/modbus.py", line 105, in __read_registers
raise FaultState.error(__name__+" "+str(type(e))+" " +
modules.common.fault_state.FaultState: ("modules.common.modbus <class 'modules.common.fault_state.FaultState'> ('modules.common.modbus Exception Response(131, 3, IllegalValue)', <FaultStateLevel.ERROR: 2>)", <FaultStateLevel.ERROR: 2>)
2024-02-03 16:08:11,055 - {modules.common.component_context:24} - {DEBUG:component1} - Update Komponente ['Huawei Wechselrichter']
2024-02-03 16:08:11,058 - {modules.common.component_context:24} - {DEBUG:update values cp2} - Update Komponente ['Ladepunkt']
2024-02-03 16:08:11,157 - {modules.common.component_context:24} - {DEBUG:component0} - Update Komponente ['Huawei Zähler']
2024-02-03 16:08:11,207 - {helpermodules.setdata:339} - {ERROR:Setdata} - Payload ungültig: Topic openWB/set/chargepoint/2/get/soc, Payload None darf nicht 'None' sein.
2024-02-03 16:08:11,214 - {helpermodules.setdata:339} - {ERROR:Setdata} - Payload ungültig: Topic openWB/set/chargepoint/2/get/soc_timestamp, Payload None darf nicht 'None' sein.
2024-02-03 16:08:11,322 - {modules.ripple_control_receiver:30} - {DEBUG:MainThread} - RSE1-Status: False, RSE2-Status: False
2024-02-03 16:08:11,324 - {control.counter:138} - {INFO:MainThread} - Verbleibende Ströme an Zähler 0: [35.0, 35.0, 35.0]A
2024-02-03 16:08:11,325 - {control.counter:161} - {INFO:MainThread} - Verbleibende Leistung an Zähler 0: 24046.0W
2024-02-03 16:08:11,328 - {control.chargepoint.chargepoint:277} - {INFO:MainThread} - LP 2: Keine Ladung, da kein Auto angesteckt ist.
2024-02-03 16:08:11,332 - {modules.common.simcount._simcount:38} - {DEBUG:MainThread} - Previous state: SimCounterState(timestamp=1705480173.8526406, power=0, imported=0.0, exported=0)
2024-02-03 16:08:11,337 - {modules.common.simcount._calculate:13} - {DEBUG:MainThread} - time passed: 414.644, power1: 0, power2: 42
2024-02-03 16:08:11,338 - {modules.common.simcount._calculate:29} - {DEBUG:MainThread} - power did not change sign. Total energy: 8707.52
2024-02-03 16:08:11,338 - {modules.common.simcount._simcount:47} - {DEBUG:MainThread} - imported: 8707.52 Wh, exported: 0 Wh, new state: SimCounterState(timestamp=1706972891.332088, power=42, imported=8707.518630109627, exported=0)
2024-02-03 16:08:11,341 - {control.data:236} - {INFO:MainThread} - bat_all_data
BatAllData(config=Config(configured=False), get=Get(soc=0, daily_exported=0, daily_imported=0, fault_str='Kein Fehler.', fault_state=0, imported=0, exported=0, power=0), set=Set(charging_power_left=0, switch_on_soc_reached=False))
2024-02-03 16:08:11,342 - {control.data:237} - {INFO:MainThread} - cp_all_data
AllChargepointData(get=AllGet(daily_imported=0.0, daily_exported=0, power=0, imported=7231752.93, exported=0))
2024-02-03 16:08:11,344 - {control.data:266} - {INFO:MainThread} - cp2
ChargepointData(control_parameter=ControlParameter(chargemode=<Chargemode.STOP: 'stop'>, current_plan=None, imported_at_plan_start=None, imported_instant_charging=None, limit=None, phases=0, prio=False, required_current=0, required_currents=[0.0, 0.0, 0.0], state=<ChargepointState.NO_CHARGING_ALLOWED: 0>, submode=<Chargemode.STOP: 'stop'>, timestamp_auto_phase_switch=None, timestamp_perform_phase_switch=None, timestamp_switch_on_off=None), get=Get(charge_state=False, connected_vehicle=ConnectedVehicle(config=ConnectedConfig(average_consumption=17, charge_template=0, chargemode='stop', current_plan=0, ev_template=0, priority=False, time_charging_in_use=False), info=ConnectedInfo(id=0, name='Ladepunkt'), soc=ConnectedSoc(fault_str='Kein Fehler.', fault_state=0, range_charged=0, range_unit='km', range=0, soc=0, timestamp=None)), currents=[0.0, 0.0, 0.0], daily_imported=0.0, daily_exported=0, evse_current=0, exported=0, fault_str='Kein Fehler.', fault_state=0, imported=7231752.93, phases_in_use=0, plug_state=False, power=0, rfid_timestamp=None, rfid=None, soc=None, soc_timestamp=None, state_str='Keine Ladung, da kein Auto angesteckt ist.', voltages=[238.72, 238.3, 238.67]), set=Set(change_ev_permitted=False, charging_ev=-1, charging_ev_prev=-1, current=0, energy_to_charge=0, loadmanagement_available=True, log=Log(chargemode_log_entry='_', imported_at_mode_switch=0, imported_at_plugtime=0, imported_since_mode_switch=0, imported_since_plugged=0, range_charged=0, time_charged='00:00', timestamp_start_charging=None), manual_lock=False, phases_to_use=0, plug_state_prev=False, plug_time=None, required_power=0, rfid=None, target_current=0, charging_ev_data=<control.ev.Ev object at 0x7153fe80>), config=Config(configuration={'mode': 'series', 'ip_address': 'localhost', 'duo_num': 0}, ev=0, name='Interne openWB', type='internal_openwb', template=0, connected_phases=3, phase_1=0, auto_phase_switch_hw=False, control_pilot_interruption_hw=False, id=2))
2024-02-03 16:08:11,346 - {control.data:266} - {INFO:MainThread} - cpt0
CpTemplateData(autolock=Autolock(active=False, plans={}, wait_for_charging_end=False), id=0, max_current_multi_phases=32, max_current_single_phase=32, name='Standard Ladepunkt-Profil', rfid_enabling=False, valid_tags=[])
2024-02-03 16:08:11,347 - {control.data:266} - {INFO:MainThread} - cpt1
CpTemplateData(autolock=Autolock(active=False, plans={}, wait_for_charging_end=False), id=1, max_current_multi_phases=32, max_current_single_phase=32, name='Standard Ladepunkt-Profil 2', rfid_enabling=False, valid_tags=[])
2024-02-03 16:08:11,348 - {control.data:266} - {INFO:MainThread} - counter0
CounterData(config=Config(max_currents=[35, 35, 35], max_total_power=24000), get=Get(powers=[0.0, 0.0, 0.0], currents=[0.0, 0.0, 0.0], voltages=[230.0, 230.0, 230.0], power_factors=[0.0, 0.0, 0.0], unbalanced_load=0, frequency=0, daily_exported=0, daily_imported=0, imported=0, exported=0, fault_state=2, fault_str="modules.common.modbus <class 'modules.common.fault_state.FaultState'> ('modules.common.modbus Exception Response(131, 3, IllegalValue)', <FaultStateLevel.ERROR: 2>)", power=0), set=Set(error_counter=1, reserved_surplus=0, released_surplus=0, raw_power_left=24046.0, raw_currents_left=[35.0, 35.0, 35.0], surplus_power_left=0, state_str=''))
2024-02-03 16:08:11,349 - {control.data:241} - {INFO:MainThread} - counter_all_data
CounterAllData(config=Config(reserve_for_not_charging=False), get=Get(hierarchy=[{'id': 0, 'type': 'counter', 'children': [{'id': 1, 'type': 'inverter', 'children': []}, {'id': 2, 'type': 'cp', 'children': []}]}]), set=Set(loadmanagement_active=False, home_consumption=42, invalid_home_consumption=0, daily_yield_home_consumption=0.0, imported_home_consumption=8707.518630109627, disengageable_smarthome_power=0))
2024-02-03 16:08:11,350 - {control.data:266} - {INFO:MainThread} - ct0
ChargeTemplateData(name='Standard-Lade-Profil', disable_after_unplug=False, prio=False, load_default=False, time_charging=TimeCharging(active=False, plans={}), chargemode=Chargemode(selected='stop', pv_charging=PvCharging(min_soc_current=10, min_current=0, feed_in_limit=False, min_soc=0, max_soc=100), scheduled_charging=ScheduledCharging(plans={}), instant_charging=InstantCharging(current=10, limit=Limit(selected='none', amount=1000, soc=50))))
2024-02-03 16:08:11,352 - {control.data:266} - {INFO:MainThread} - ev0
EvData(set=Set(ev_template=EvTemplate(data=EvTemplateData(name='Standard-Fahrzeug-Profil', max_current_multi_phases=16, max_phases=3, phase_switch_pause=2, prevent_phase_switch=False, prevent_charge_stop=False, control_pilot_interruption=False, control_pilot_interruption_duration=4, average_consump=17000, min_current=6, max_current_single_phase=32, battery_capacity=82000, efficiency=90, nominal_difference=1, keep_charge_active_duration=40), et_num=0), soc_error_counter=0), charge_template=0, ev_template=0, name='Standard-Fahrzeug', tag_id=[], get=Get(soc=0, soc_timestamp=None, force_soc_update=False, range=0, fault_state=0, fault_str='Kein Fehler.'))
2024-02-03 16:08:11,353 - {control.data:266} - {INFO:MainThread} - et0
EvTemplateData(name='Standard-Fahrzeug-Profil', max_current_multi_phases=16, max_phases=3, phase_switch_pause=2, prevent_phase_switch=False, prevent_charge_stop=False, control_pilot_interruption=False, control_pilot_interruption_duration=4, average_consump=17000, min_current=6, max_current_single_phase=32, battery_capacity=82000, efficiency=90, nominal_difference=1, keep_charge_active_duration=40)
2024-02-03 16:08:11,354 - {control.data:245} - {INFO:MainThread} - general_data
GeneralData(chargemode_config=ChargemodeConfig(instant_charging=InstantCharging(phases_to_use=1), pv_charging=PvCharging(bat_prio=True, charging_power_reserve=200, control_range=[0, 230], feed_in_yield=15000, phase_switch_delay=7, phases_to_use=1, rundown_power=1000, rundown_soc=50, switch_off_delay=60, switch_off_soc=40, switch_off_threshold=50, switch_on_delay=30, switch_on_soc=60, switch_on_threshold=1500), scheduled_charging=ScheduledCharging(phases_to_use=0), time_charging=TimeCharging(phases_to_use=1), unbalanced_load_limit=18, unbalanced_load=False), control_interval=60, extern_display_mode='primary', extern=False, external_buttons_hw=False, grid_protection_active=False, grid_protection_configured=True, grid_protection_random_stop=0, grid_protection_timestamp='', mqtt_bridge=False, price_kwh=0.3, range_unit='km', ripple_control_receiver=RippleControlReceiver(configured=True, r1_active=False, r2_active=False))
2024-02-03 16:08:11,355 - {control.data:246} - {INFO:MainThread} - general_data-display
primary
2024-02-03 16:08:11,356 - {control.data:247} - {INFO:MainThread} - graph_data
GraphData(config=Config(duration=120))
2024-02-03 16:08:11,357 - {control.data:248} - {INFO:MainThread} - optional_data
OptionalData(et=Et(active=False, config=EtConfig(max_price=0, provider={}), get=EtGet(price=0, price_list=[])), int_display=InternalDisplay(active=False, on_if_plugged_in=True, pin_active=False, pin_code='0000', standby=60, theme=<modules.display_themes.cards.config.CardsDisplayTheme object at 0x7154f9d0>), led=Led(active=False), rfid=Rfid(active=False))
2024-02-03 16:08:11,358 - {control.data:266} - {INFO:MainThread} - pv1
PvData(config=Config(max_ac_out=0), get=Get(currents=[0.0, 0.0, 0.0], daily_exported=0, monthly_exported=0, yearly_exported=0, exported=0, fault_state=2, fault_str="modules.common.modbus <class 'modules.common.fault_state.FaultState'> ('modules.common.modbus Exception Response(131, 3, IllegalValue)', <FaultStateLevel.ERROR: 2>)", power=-42))
2024-02-03 16:08:11,358 - {control.data:250} - {INFO:MainThread} - pv_all_data
PvAllData(config=Config(configured=True), get=Get(daily_exported=0, monthly_exported=0, yearly_exported=0, exported=0, power=-42))
2024-02-03 16:08:11,360 - {control.data:266} - {INFO:MainThread} - system
{'update_in_progress': False, 'perform_update': False, 'ip_address': '10.10.1.223', 'current_commit': '2024-01-03 12:21:20 +0100 [06bcf54f9]', 'current_branch': 'Release', 'current_branch_commit': '2024-01-03 12:21:20 +0100 [06bcf54f9]', 'current_missing_commits': [], 'datastore_version': 29, 'dataprotection_acknowledged': True, 'usage_terms_acknowledged': True, 'debug_level': 10, 'release_train': 'master', 'version': '2.1.2-Patch.2', 'boot_done': True, 'lastlivevaluesJson': {'timestamp': 1705480173, 'time': '09:29:33', 'house-power': 0.0, 'charging-all': 0.0, 'pv-all': -0.0, 'cp2-power': 0.0}, 'module_update_completed': True}
2024-02-03 16:08:11,361 - {control.data:279} - {INFO:MainThread} - device0
{'name': 'Huawei', 'type': 'huawei', 'id': 0, 'configuration': {'modbus_id': 1, 'ip_address': '10.10.1.66'}}
2024-02-03 16:08:11,362 - {control.data:281} - {INFO:MainThread} - component0
{'name': 'Huawei Zähler', 'type': 'counter', 'id': 0, 'configuration': {}}
2024-02-03 16:08:11,363 - {control.data:281} - {INFO:MainThread} - component1
{'name': 'Huawei Wechselrichter', 'type': 'inverter', 'id': 1, 'configuration': {}}
2024-02-03 16:08:11,363 - {control.data:253} - {INFO:MainThread} -
2024-02-03 16:08:11,364 - {control.algorithm.algorithm:25} - {INFO:MainThread} - # Algorithmus
2024-02-03 16:08:11,365 - {control.algorithm.algorithm:30} - {INFO:MainThread} - **Mindestrom setzen**
2024-02-03 16:08:11,368 - {control.algorithm.algorithm:32} - {INFO:MainThread} - **Sollstrom setzen**
2024-02-03 16:08:11,369 - {control.counter:211} - {INFO:MainThread} - Überschuss zur PV-geführten Ladung: 0W
2024-02-03 16:08:11,370 - {control.counter:457} - {DEBUG:MainThread} - Zähler 0: Begrenzung der verbleibenden Leistung auf 0W
2024-02-03 16:08:11,371 - {control.algorithm.algorithm:43} - {INFO:MainThread} - **Keine Leistung für PV-geführtes Laden übrig.**
2024-02-03 16:08:11,371 - {control.process:23} - {INFO:MainThread} - # Ladung starten.
2024-02-03 16:08:11,374 - {modules.common.component_context:24} - {DEBUG:set current cp2} - Update Komponente ['Ladepunkt']
2024-02-03 16:08:11,392 - {control.counter:186} - {INFO:MainThread} - 0W reservierte EVU-Leistung, 0W freigegebene EVU-Leistung
2024-02-03 16:08:11,569 - {schedule:660} - {DEBUG:MainThread} - Running job Job(interval=1, unit=minutes, do=smarthome_handler, args=(), kwargs={})
2024-02-03 16:08:11,571 - {root:56} - {DEBUG:MainThread} - Don't start multiple instances of smarthome thread.
2024-02-03 16:08:15,581 - {schedule:660} - {DEBUG:MainThread} - Running job Job(interval=1, unit=minutes, do=smarthome_handler, args=(), kwargs={})
2024-02-03 16:08:16,108 - {helpermodules.setdata:641} - {WARNING:Setdata} - Kein Wechselrichter 5 mit gültiger Konfiguration gefunden.
2024-02-03 16:08:20,595 - {schedule:660} - {DEBUG:MainThread} - Running job Job(interval=1, unit=minutes, do=handler10Sec, args=(), kwargs={})
2024-02-03 16:08:20,596 - {root:74} - {INFO:MainThread} - # ***Start***