Protoss PE11-H configuration ?

Fragen zur Nutzung, Features, usw..
courage2000
Beiträge: 57
Registriert: Fr Jun 05, 2020 10:37 pm

Protoss PE11-H configuration ?

Beitrag von courage2000 »

Hello!

I have one SDM630Modbus V2 for my EVSE-WIFI, connected to a Protoss PE11-H Modbus- > TCP converter.

That changes I must do to the Protoss configuration?

Thank you.

Here are my settings. Do I need to change something?

Thank you!
11.png
22.png
HSC
Beiträge: 3941
Registriert: So Jan 10, 2021 8:49 am

Re: Protoss PE11-H configuration ?

Beitrag von HSC »

Here is a problem:
Screenshot_20210911-145046_Chrome.jpg
Wait pleace 1 min....
HSC
Beiträge: 3941
Registriert: So Jan 10, 2021 8:49 am

Re: Protoss PE11-H configuration ?

Beitrag von HSC »

There is a .pdf:
viewtopic.php?p=45047#p45047

The same konfig for the sdm 630: 9600, ID xxx, none.
🙋‍♂️
HSC
Beiträge: 3941
Registriert: So Jan 10, 2021 8:49 am

Re: Protoss PE11-H configuration ?

Beitrag von HSC »

Screenshot_20210911-145814_Chrome.jpg
courage2000
Beiträge: 57
Registriert: Fr Jun 05, 2020 10:37 pm

Re: Protoss PE11-H configuration ?

Beitrag von courage2000 »

So
Local port: 8899

Thank you
HSC
Beiträge: 3941
Registriert: So Jan 10, 2021 8:49 am

Re: Protoss PE11-H configuration ?

Beitrag von HSC »

👍
derNeueDet
Beiträge: 4237
Registriert: Mi Nov 11, 2020 7:16 pm

Re: Protoss PE11-H configuration ?

Beitrag von derNeueDet »

That depends which which module you want to use it.
8899 is usually used in openWB, but you are referencing EVSE Wifi.

Best regards
Det
10kWp PV mit SMA Tripower 10000TL-10 (PE11 mit SDM72V2); 2,4kWp mit Solis 2.5 G6 (EE11 mit SDM120). OpenWB Standard+. EVU EM540 an einem Raspi mit Venus OS. BEV Mercedes EQA 250 (07/2023)
HSC
Beiträge: 3941
Registriert: So Jan 10, 2021 8:49 am

Re: Protoss PE11-H configuration ?

Beitrag von HSC »

For what or in which module do you want to use the SDM 630?
Will it be used with openWB software?
Many greetings
courage2000
Beiträge: 57
Registriert: Fr Jun 05, 2020 10:37 pm

Re: Protoss PE11-H configuration ?

Beitrag von courage2000 »

I will try OpenWB and EVCC.
derNeueDet
Beiträge: 4237
Registriert: Mi Nov 11, 2020 7:16 pm

Re: Protoss PE11-H configuration ?

Beitrag von derNeueDet »

To use it in openWB as a meter to measure the powerflow from or to the grid, you have to use it as
EVU Kit type SDM and that needs a special setup of the IP address and of the unit_id.

IPAddress: 192.168.193.15
Port: 8899
Unit_id: 115

Best regards
Det
10kWp PV mit SMA Tripower 10000TL-10 (PE11 mit SDM72V2); 2,4kWp mit Solis 2.5 G6 (EE11 mit SDM120). OpenWB Standard+. EVU EM540 an einem Raspi mit Venus OS. BEV Mercedes EQA 250 (07/2023)
Antworten